Example 2-5:

A 15-kVA, 2300/230-V transformer is to be tested (short circuit & open circuit tests as shown

below) to determine its excitation branch components, its series impedances, and its voltage

regulation (See figures below):

+ +

!" !# $# $"

2300V 230V

+ +

!%& !# $# $"

2300V 230V

'%&

()*

+

!+* $# $"

2300V 230V

'"&

()*

The following test data have been taken from the transformer:

Open-circuit test

(High voltage side open)

Short-circuit test

(Low voltage side shorted)

,!-. = 230,! !/. = 47,!

'-. = 215,6 '/. = 810,6

(-. = 90,: (/. = 580,:

(a) --- Find the equivalent circuit for this transformer referred to the high-voltage side.

(b) --- Find the equivalent circuit for this transformer referred to the low-voltage side.

(c) --- Calculate the full-load voltage regulation at 0.8 lagging power factor, unity power factor & at

0.8 leading power factor using the exact equation for,!; --- Do a phasor diagram for each case

(d) --- Plot the voltage regulation as load is increased from no-load to-full load at power factors of

0.8 lagging, unity, and 0.8 leading.

(e) --- Find the efficiency of the transformer at full load with a power factor of 0.8 lagging

45

Solution --- The figure at left & the eq’s are repeated from previous page(s):

+ +

!%& !# $# $"

2300V 230V

'%&

()*

<" >"

>?

@2

'%&

!%&

+

(%&

<*

@2

<#

@2

>#

@2

'%&

!%&

+

(%&

>?

@2

<*

@2

15 KVA, 2300/230-V (Transformer Rating) --- [ !-. = 230,!A '-. = 215,6A (-. = 90,:]

----------------------------------------------------------------------------------------------------------------------------------

(a) --- Find the equivalent circuit of this transformer referred to the high-voltage side:

From the figures at left, we have:

@ = 2300B230 = 50 (The turn-ratio or, the voltage-ratio)

Use the OC-test to find the shunt parameters:

· The figure above (middle) shows the circuit for the OC-test case

· The figure above (right) shows the approximate circuit for the OC-test case --- Using this circuit:

C-. = cos DE ;FG

HFG,I ! = cos"#

$%&'

()*%&+,().#&-, = 84°

/0 = |1 !&|

|+ !| &&2 3 567 --- The excitation admittance or, the shunt admittance

= ).#&-

)*%&+ 2 3 84°&9 = :.::;<>&2 3 84°&9 = :.:::;?4 3 @:.::;:8&9 = &ABCD 3 @EFCD

G

HBCD = #

IJCK =

#

%.%%%L$M = <:?:&N --- The value of&HB referred to the secondary

OFCD = #

PQCK =

#

%.%%L%R = <<:&N --- The value of&OF referred to the secondary

46

Solution [Continued] --- The first two figures and the eq’s are repeated from previous page(s):

+

3 S9T UV UW

2300V 230V

XWY

Z[T

HV @OV \2HW @\2OW

@O] HY

XV

SV

3

+

XW

\

H^_V @O^_V XV

SV

3

+

XW

\

\ = `>::a`>: = <:

15 KVA, 2300/230-V --- Transformer Rating

[Sb7 = 4d&S , Xb7 = e.:&f , Zb7 =

----------------------------------------------------------------------------------------------------------------------------------

(a) --- Find the equivalent circuit of this transformer referred to the high-voltage side [Continued]:

Use the SC-test to find the series parameters:

· The figure above (middle) shows the circuit for the SC-test case

· The figure above (right) shows the approximate circuit for the SC-test case --- Using this circuit:

5b7 = cos "# hi!

+i!&1i! = cos"#

#j%&'

(Mk&+,(j&-, = ??.4° --- The series impedance angle

lb0 = &|+i!&|

|1i!| &25b7 --- The equivalent series impedance

= Mk&+2$$.M°&

j&- = d.8>>2??.4° = 4.4? m @e.4?&N = HnpCh m @OnpCh

G

HnpCh = 4.4?&N & OnpCh = e.4?&N --- The series elements referred to the primary side

47

Solution [Continued] --- The first figure & the eq’s are repeated from previous page(s):

+ +

3 3

SW SV UV UW

2300V 230V

\ = `>::a`>: = <:

H7Cb = <:?:&N & OFCb = <<:&N (The values are of referred to the secondary)

HnpCh = 4.4?&N & OnpCh = e.4?&N (The values are of referred to the primary)

----------------------------------------------------------------------------------------------------------------------------------

(a) --- Find the equivalent circuit of this transformer referred to the high-voltage side [Continued]:

· Next, we need to bring the shunt elements to the primary (or, high-voltage) side:

H7Ch = \ )&H7Cb = (<:,

)(<:?:&N, = <:?&qN & OFCh = \ )&OFCb = (<:,

)(<<:&N, = <<&qN

· This equivalent circuit is shown in figure above, middle

(b) --- Find the equivalent circuit of this transformer referred to the low-voltage side (secondary):

· We have previously found the shunt components referred to secondary and the series

components referred to primary --- See above

· So, in order to find the model referred to secondary, we need to refer the series components

to the secondary as follows:

HnpCb = rtuCv

&wx =

. !"#

"($%)& = 0.0445"' & *+,-/ =

123-6 "7&

= 8. !"# "($%)&

= 0.0945"'

The resulting equivalent circuit is shown in figure above, right.

48

Solution [Continued] --- Repeated from previous page(s):

+ +

: :

;< ;> ?> ?<

2300V 230V

15 KVA, 2300/230-V Referred to primary Referred to secondary

;@ = A6 7B CAD-EF

AD-EF × G00

----------------------------------------------------------------------------------------------------------------------------------

(c) --- Calculate the full-load voltage regulation at 0.8 lagging power factor, unity power factor, and

at 0.8 leading power factor:

H/-I7J+K = /LMN2O AD-LMN2O

= $!-%%%"AP QR%"A

= 95.S"T (The magnitude of the full-load current on secondary side)

UV = "0.W (Lagging): H/ = |H/|"X : YZ

A6 7 = ;/ ^ @+,H/ ^ _*+,H/ --- ;/ = S\0X0°"; (Full-load secondary voltage)

= S\0X0°"; ^ (0.0445"')`95.SX : \9.]°"Ta ^ _(0.0945"')`95.SX : \9.]°"Ta = S\0X0°"; ^ S.]0X : \9.]°"; ^ 4.SGX5\.G°"; = S\0 ^ S.\S : _G.b4 ^ S.5S ^ _\.\9 = S\4.W4 ^ _G.9S = S\4.W5X0.40° (Full-load primary voltage, referred to secondary) Now,

;@ = A6 7B CAD-EF

AD-EF × G00 = QR .c!"ACQR%"A

QR%"A × G00d = S.Gd (The voltage regulation)

49

Solution [Continued] --- Repeated from previous page(s): 15 KVA, 2300/230-V (Transformer Rating)

+ +

: :

;< ;> ?> ?<

2300V 230V

----------------------------------------------------------------------------------------------------------------------------------

(c) --- Calculate the full-load voltage regulation at 0.8 lagging power factor, unity power factor, and

at 0.8 leading power factor [Continued]:

UV = "G (Unity): H/ = |H/|"X : YZ

= S\0X0°"; ^ S.]0X0°"; ^ 4.SGX]0° = S\0 ^ S.]0 ^ _4.SG = S\S.] ^ _4.SG = S\S.]4XG.04° [ ;@ =

A6 7B CAD-EF AD-EF

× G00"" = QRQ.g "ACQR%"A QR%"A

× G00d = G.SWd (The voltage regulation)

UV = "0.W (Leading): H/ = |H/|"X ^ YZ

A6 7 = S\0X0°"; ^ (0.0445"')`95.SX\9.]°"Ta ^ _(0.0945"')`95.SX\9.]°a

= S\0X0°"; ^ S.]0X\9.]°"; ^ 4.SGXGS9.]°"; = S\0 ^ S.\S ^ _G.S4 : S.5S ^ _\.\9 = SS].W0 ^ _5.G0 = SS].W5XG.Sb°"; [ ;@ =

A6 7B CAD-EF AD-EF

× G00""" = QQg.c!"ACQR%"A QR%"A

× G00d = :0.09Sd (The voltage regulation)

50

Solution [Continued] --- Repeated from previous page(s): 15 KVA, 2300/230-V (Transformer Rating)

+ +

: :

;< ;> ?> ?<

2300V 230V

----------------------------------------------------------------------------------------------------------------------------------

(c) --- Calculate the full-load voltage regulation at 0.8 lagging power factor, unity power factor, and

at 0.8 leading power factor --- Do a phasor diagram for each case:

A6 7 = ;/ ^ @+,H/ ^ _*+,H/ --- Using the figure above at right

· We have all components of the above equation (as shown in the above figure, right)

· We also, found the currents for the 3 cases of 0.8 lagging power factor, unity power factor,

and 0.8 leading power factor

· Using these values, we simply show the above equation using phasors --- Each of these three

phasor diagrams is shown in figures below:

51

Solution [Continued] --- Repeated from previous page(s):

+ +

: :

;< ;> ?> ?<

2300V 230V

----------------------------------------------------------------------------------------------------------------------------------

(d) --- Plot the voltage regulation as load is increased from no-load to-full load at power factors of

0.8 lagging, unity, and 0.8 leading:

The best way to plot the voltage regulation as a function of load is to repeat the calculations

presented in part (c) for many different values of the loads by writing a MATLAB program (See

your text) --- The plot produced by this program is shown in figure below:

;@ = A6 7 B CAD AD

× G00 ---

· Can you interpret these curves?

· Do this part and submit a report (See Design 1)

52

Solution [Continued] --- Repeated from previous page(s): 15 KVA, 2300/230-V (Transformer Rating)

+ +

: :

;< ;> ?> ?<

2300V 230V

H/ = 95.S"X : \9.]°"T (Full-load current for the case of power factor of 0.8 lagging)

h = eijN eFikkl !"#

× 100% = !"#

( $"& '!)*+& !"# × 100% --- The efficiency at this condition

----------------------------------------------------------------------------------------------------------------------------------

(e) --- Find the efficiency of the transformer at full load with a power factor of 0.8 lagging:

To find the transformer efficiency of the transformer, we calculate its output power and

its losses --- Using the circuit at right:

,-. = |/2| 3456 = (789:;<+

3(090>>8;?+ = 1@A;B (The copper losses)

,-CD5 = ;|EF GH |

I

J$

KI

= (3LM9NO;E+I

PQOQ;R = 8:98;B (The core losses)

,S.T = |U2||/2|;,V (The output power of the transformer at this power factor)

= (:W0;U+(789:;<+09@ = 1:X000;B

Finally, the efficiency is:

Y = Z"#

( $";&; $!)*+;&; Z"# × 100% =

P3XQQQ;[

(PN\;[;&;O39O;[+;&;P3XQQQ;[ × 100% = A@90W%

53

Design 1 [Due next week today]:

This design is related to the previous example problem --- Figures below are repeated:

+ +

] ]

Û U_ _̀ ^̀

2300V 230V

----------------------------------------------------------------------------------------------------------------------------------

(1) --- Plot the voltage regulation of the transformer as its loading is increased from no-load to full-

load at power factors of 0.8 lagging, unity, and 0.8 leading --- This is part (d) of the previous

example problem (You should plot the 3 curves in one graph for easy comparison)

(2) --- Plot the efficiency of the transformer as its load is increased from no-load to-full load at

power factors of 0.8 lagging, unity, and 0.8 leading --- This is part (e) of the previous example

problem, but extended to include the various loading as well as loads with the unity, and

leading power factors (You should plot the 3 curves in one graph for easy comparison)

(3) --- Prepare a report including: a summary of the problem, your MATLAB code, the plots and an

engineering conclusion derived from each of the plots

(4) --- The report should be submitted to me via email (Gradman@TNTech.edu) in one PDF-file and

the file should be named as follows:

Your class no -- Your last name -- Design 1 -- ECE 3610 -- Summer 2017

For example, assume my number is 99 --- Then, I will name my PDF-file as follows:

99 -- Radman -- Design 1 -- ECE 3610 -- Summer 2017

Homework is Completed By:

Writer Writer Name Amount Client Comments & Rating
Instant Homework Helper

ONLINE

Instant Homework Helper

$36

She helped me in last minute in a very reasonable price. She is a lifesaver, I got A+ grade in my homework, I will surely hire her again for my next assignments, Thumbs Up!

Order & Get This Solution Within 3 Hours in $25/Page

Custom Original Solution And Get A+ Grades

  • 100% Plagiarism Free
  • Proper APA/MLA/Harvard Referencing
  • Delivery in 3 Hours After Placing Order
  • Free Turnitin Report
  • Unlimited Revisions
  • Privacy Guaranteed

Order & Get This Solution Within 6 Hours in $20/Page

Custom Original Solution And Get A+ Grades

  • 100% Plagiarism Free
  • Proper APA/MLA/Harvard Referencing
  • Delivery in 6 Hours After Placing Order
  • Free Turnitin Report
  • Unlimited Revisions
  • Privacy Guaranteed

Order & Get This Solution Within 12 Hours in $15/Page

Custom Original Solution And Get A+ Grades

  • 100% Plagiarism Free
  • Proper APA/MLA/Harvard Referencing
  • Delivery in 12 Hours After Placing Order
  • Free Turnitin Report
  • Unlimited Revisions
  • Privacy Guaranteed

6 writers have sent their proposals to do this homework:

Accounting & Finance Specialist
Academic Mentor
Engineering Help
Quality Homework Helper
Supreme Essay Writer
Math Specialist
Writer Writer Name Offer Chat
Accounting & Finance Specialist

ONLINE

Accounting & Finance Specialist

I have read your project details and I can provide you QUALITY WORK within your given timeline and budget.

$31 Chat With Writer
Academic Mentor

ONLINE

Academic Mentor

I am an experienced researcher here with master education. After reading your posting, I feel, you need an expert research writer to complete your project.Thank You

$41 Chat With Writer
Engineering Help

ONLINE

Engineering Help

I am an elite class writer with more than 6 years of experience as an academic writer. I will provide you the 100 percent original and plagiarism-free content.

$40 Chat With Writer
Quality Homework Helper

ONLINE

Quality Homework Helper

I find your project quite stimulating and related to my profession. I can surely contribute you with your project.

$23 Chat With Writer
Supreme Essay Writer

ONLINE

Supreme Essay Writer

I find your project quite stimulating and related to my profession. I can surely contribute you with your project.

$29 Chat With Writer
Math Specialist

ONLINE

Math Specialist

I will be delighted to work on your project. As an experienced writer, I can provide you top quality, well researched, concise and error-free work within your provided deadline at very reasonable prices.

$39 Chat With Writer

Let our expert academic writers to help you in achieving a+ grades in your homework, assignment, quiz or exam.

Similar Homework Questions

Jcu timetable - Civil and environmental engineering uts atar - Fanuc teach pendant cable pinout - Tony dungy as a leader - ECON Forum Replies - Diamond supramax external 56k usb modem - Judith myers tombstone dead by daylight - Baking soda vinegar balanced equation - Overflow relief gully australian standards - Who offers Legitimate Criminology Essay Writing Services? - Cellular respiration sumanasinc - Pumpkin rhymes and fingerplays - Organizational behavior 4th edition pdf free - A3 management process template - Vet documents for quality assurance - 615_IP5 - Three ways that thermal energy is transferred - Chapter 21 accounting for leases solutions - Chatham county building safety and regulatory services savannah ga - Family Information Night Presentation and Communication Plan - Legal aspects of nursing course - St hildas parent lounge - 10's complement of 00000 - 118 bus timetable manchester - Major service with accompanying minor goods and services - Luqman medical centre walsall - Final exam - Kal sangra houses for sale - The bradford company issued 12 bonds - What is albert pujols saying in the stubhub commercial - Discussion - Hard rock cafe forecasting case study - Advantages and disadvantages of r programming language - Www footprintnetwork org en index php gfn page personal footprint - Discussion - Cups and arms checklist - The glass castle quotes with page numbers - Dietary fats and blood cholesterol levels worksheet answers - 14 baraga grove modbury heights - A portrait of linear algebra 3rd edition pdf - Paper review - Strengths and weaknesses of the psychodynamic perspective - Maestro air 30cm mist fan - Chapter 6 jekyll and hyde - 7 habits of highly effective college students looseleaf 2nd 19 - Selection criteria examples marketing - This assessment task requires you to critically evaluate at least 4 articles posted in the blog section of Interact. however you must evaluate at least 4 items (320 words each posting). - Brk carbon monoxide alarm instructions - Restorative justice 4 schools - Ethics - One hundred years of solitude synopsis - World literature2 - Ethical standards in the human services field - Klip lok classic 700 - Jeremy kyle show foxy bingo - Animal testing persuasive speech outline - Art during the 1920s - 5th Amendment - Vce accounting study design - No soil cultivation crossword - Find a friend lyrics elizabeth bedford - Functional requirements for online cab booking - History of astronomy worksheet answers - Audit sampling software - How to calculate lateness in excel - Quadrat sampling lab answers - 39.50 dollars in pounds - Finance discussion questions - Bettermix gluten free suet - Advanced higher chemistry learning outcomes - Does hcf cover physiotherapy - An item is ________ if it is likely to influence the decision of an investor or creditor. - Buzz marketing has become a pervasive persuasion strategy because - Multiple sclerosis and type 1 diabetes an unlikely alliance - Ibm 8202 e4c end of support - Grant and cutler at foyles - Muslim Molvi 7340613399 OnLine No 1 FaMOUs VashIKaraN sPecIaLIsT IN Ahmednagar - Lady macbeth appearance vs reality - Calorimetry lab data sheet answer key - Forced choice preference assessment - You are the head of the project selection team at simsox - Who am i outline - Unit product cost under absorption costing - Plan a vacation project - Waterproofing compliance certificate nsw - Assignment 5 employee compensation and benefits - Patophysiology Topic 1 DQ2 - Busineess managment - Excel descriptive statistics confidence level - Whiteside and knowles solicitors - Acids vs Bases - Blanka dobrynin - Project management at arnold palmer hospital case study - Responsibilities, Duties, and the Operational and Management Challenges Confronting Security Directors - Discharged for off duty behavior - Coming of age ideas - Promises like pie crust christina rossetti - May lee chai saving sourdi pdf - Worksheet on electronic configuration - What is the present value of the following cash flow stream at a rate of 12.0%?